manniste
9
Indlæg: 53 Tilmeldt: 09 jan 2016 13:35
Senest aktiv: 13 nov 2016 07:35
Indlæg
af manniste » 17 jan 2016 11:24
At least something is normal
So right now it runs pretty ok when using power up to 80%, more than that it goes bananas with the fat flame.
Would this extra oxygen controller even fix my issue?
http://www.nbe-shop.dk/index.php/traepi ... m_store=da
MHES
Indlæg: 88 Tilmeldt: 17 jan 2007 21:36
Senest aktiv: 17 jun 2018 08:53 Mit fyr: RTB 10 kW
Areal: 250 m2
Fremviser gerne i postnummer: 4180
Årligt forbrug: 5,5 ton
Geografisk sted: Sorø
Blevet takket: 1 gang
Indlæg
af MHES » 17 jan 2016 11:55
Whar are the fan-values when you can run the burner OK in the range 10-80% ?
If you can't adjust the burner to burn correct at 100%, the O
2 controller can't do it either
...it can only do the same as you can
Michael
Indlæg: 10.013 Tilmeldt: 14 nov 2008 17:57
Senest aktiv: i går 19:52 Mit fyr: RTB
Har takket: 88 gange
Blevet takket: 299 gange
Indlæg
af pille bruger » 17 jan 2016 11:59
One thing we also have to check is how big ( kW ) is the burner ?
There may be a data plate next to the down pipe.
If not, how many cm is your grate ?
manniste
9
Indlæg
af manniste » 17 jan 2016 12:28
Fan values are 17,27,37 right now. And it is mostly idling around 30-60%
There is no data plate on the burner. The grate is 13.5cm wide and 20cm long.
Indlæg
af pille bruger » 17 jan 2016 12:32
manniste skrev: Fan values are 17,27,37 right now. And it is mostly idling around 30-60%
It is a 30 kW model.
numbers for blower ought to be about 10 - 20 - 30 before adjustment.
http://nbe.dk/wp-content/uploads/2015/0 ... k-97mm.pdf
Your problem could be wrong weighing 6 min.
Check weight shows the true value, and that you use the correct time.
manniste
9
Indlæg
af manniste » 17 jan 2016 13:10
Ok. Did the weighing again AND noticed this time something.
In the Auto Combustion, put it to YES for Testdrive. It shows nicely 360seconds BUT the timer start counting from 7:22 to zero. So right now it weighed 1:22 longer than 6min.
So actual 6minutes weight is 1249grams and the extra 1:22 will give 353grams more.
Inserted now value for actual 6minutes - 1249grams
And Output kw-s should I keep at 25kw or change it to 30kw (according to the size of the house).
triumph
Indlæg: 5.693 Tilmeldt: 02 aug 2011 21:08
Senest aktiv: i går 16:59 Mit fyr: 24 kw black star semirens
Årligt forbrug: 7,2 tons
Har takket: 442 gange
Blevet takket: 474 gange
Indlæg
af triumph » 17 jan 2016 13:22
The reason for 7,22 minuts for a 6 min testdrive, is that the auger stops and start during the testrun, to simulate a real production.
Your flame is to fat at high capacety. That is due to to littel air, compared to pellets.
One thing could be that the fan is not giving what it should, another could be a blocking for the air.
You said that the boiler and chimny is clean. But what about the exhastpipe from the boiler, to the chimny.
Here in demark, the guy who sweeps the chimny do not always clean this pipe ?
manniste
9
Indlæg
af manniste » 17 jan 2016 13:25
"This pipe" to the chimney I cleaned and checked 2 days ago, it was ok.
Could I measure the amount of air given by the blower or something?
So the 6min weight with 7:22 time is what I should actually use still?
When comparing to previous weighing (week ago did it) the amount has changed 167grams greater...
Senest rettet af manniste 17 jan 2016 13:32, rettet i alt 1 gang.
triumph
Indlæg
af triumph » 17 jan 2016 13:29
yes. in the 7,22 time. The auger only runs in 6 min
triumph
Indlæg
af triumph » 17 jan 2016 13:32
what is the prolem if you set the "blower high" to f.exsampel 40, instead of 37 ?