I can recommend to mount the shield on the burner.
The shield prevents the risk of electrical shock and ensures that the burner temperature is measured correctly
16-24kw burner problems
-
- Stoker II
- 9
- Indlæg: 53
- Tilmeldt: 09 jan 2016 13:35
Re: 16-24kw burner problems
Update:
Swapped both burner capacitors AND circuit board, just to be sure.
Did the new weighing - 1435g. Put everything together and turned it on...so far so good! Been running now 6h normally (at least I think it is normal
)
Cleaned all the chimney pipes and boiler, just to be sure again.
Now just need to know what kind a blower percentage should I need (low, mid, high values I mean). Right now lower slightly previous values, flame seemed to be fine.
And those P.I things, have no idea what do with that.
Swapped both burner capacitors AND circuit board, just to be sure.
Did the new weighing - 1435g. Put everything together and turned it on...so far so good! Been running now 6h normally (at least I think it is normal

Cleaned all the chimney pipes and boiler, just to be sure again.
Now just need to know what kind a blower percentage should I need (low, mid, high values I mean). Right now lower slightly previous values, flame seemed to be fine.
And those P.I things, have no idea what do with that.
-
- Supporter
- 16
- Indlæg: 10.013
- Tilmeldt: 14 nov 2008 17:57
- Mit fyr: RTB
- Areal: 160
- Brændsel: piller + 30 rør solfanger
- Dagligt forbrug: 10 kg.
- Årligt forbrug: 3400 kg.
- Geografisk sted: Svendborg
- Har takket: 88 gange
- Blevet takket: 299 gange
Re: 16-24kw burner problems
Find your blower, and numbers for your blower here http://nbe.dk/wp-content/uploads/2015/0 ... fl85mm.pdfmanniste skrev:Update:
Swapped both burner capacitors AND circuit board, just to be sure.
Did the new weighing - 1435g. Put everything together and turned it on...so far so good! Been running now 6h normally (at least I think it is normal)
Cleaned all the chimney pipes and boiler, just to be sure again.
Now just need to know what kind a blower percentage should I need (low, mid, high values I mean). Right now lower slightly previous values, flame seemed to be fine.
And those P.I things, have no idea what do with that.
Get the control on StokerKontrol, so it is easier to help with PI regulation. ( See previous link )
Best regards
Michael fra StokerCloud Support http://www.nbe.dk/sadan-fungere-stokercloud/
Find manualer her https://www.nbe.dk/manualer-nbe/
Tekniske vejledninger https://www.nbe.dk/tekniske-vejledninger/
Michael fra StokerCloud Support http://www.nbe.dk/sadan-fungere-stokercloud/
Find manualer her https://www.nbe.dk/manualer-nbe/
Tekniske vejledninger https://www.nbe.dk/tekniske-vejledninger/
-
- Stoker II
- 9
- Indlæg: 53
- Tilmeldt: 09 jan 2016 13:35
Re: 16-24kw burner problems
Current Update.
Boiler is at 62C (differences are over 5 and under 5).
Burner runs at 50%
BUT the flame looks more than 100%
and just keeps adding and adding more pellets.
It won't bring the power down just keeps idle'ing at 50% even when circulation pumps are pumping less and less (automatic flow control) because house is warm enough.
Only thing which I know to do is pull the Plug from the burner for a second. Does the "Checking" and goes to Temp Stop...
Boiler is at 62C (differences are over 5 and under 5).
Burner runs at 50%
BUT the flame looks more than 100%

It won't bring the power down just keeps idle'ing at 50% even when circulation pumps are pumping less and less (automatic flow control) because house is warm enough.
Only thing which I know to do is pull the Plug from the burner for a second. Does the "Checking" and goes to Temp Stop...
-
- Stoker II
- 9
- Indlæg: 53
- Tilmeldt: 09 jan 2016 13:35
Re: 16-24kw burner problems
Managed to connect an old pc to internet in boiler room, so now I have to do some ftp magic to get burner online. Any good advice how to get it online, I have StokerKontrol v3.1
-
- Supporter
- 16
- Indlæg: 10.013
- Tilmeldt: 14 nov 2008 17:57
- Mit fyr: RTB
- Areal: 160
- Brændsel: piller + 30 rør solfanger
- Dagligt forbrug: 10 kg.
- Årligt forbrug: 3400 kg.
- Geografisk sted: Svendborg
- Har takket: 88 gange
- Blevet takket: 299 gange
Re: 16-24kw burner problems
If you wish to be registered with it to StokerCloud server, simply contact Stokersoft on info@stokerkontrol.dk, remember to send your serial number, name and address in the email.manniste skrev:Managed to connect an old pc to internet in boiler room, so now I have to do some ftp magic to get burner online. Any good advice how to get it online, I have StokerKontrol v3.1
and get the PC online.
Best regards
Michael fra StokerCloud Support http://www.nbe.dk/sadan-fungere-stokercloud/
Find manualer her https://www.nbe.dk/manualer-nbe/
Tekniske vejledninger https://www.nbe.dk/tekniske-vejledninger/
Michael fra StokerCloud Support http://www.nbe.dk/sadan-fungere-stokercloud/
Find manualer her https://www.nbe.dk/manualer-nbe/
Tekniske vejledninger https://www.nbe.dk/tekniske-vejledninger/
-
- Stoker II
- 9
- Indlæg: 53
- Tilmeldt: 09 jan 2016 13:35
Re: 16-24kw burner problems
Yes did that email sending already yesterday evening. And upgraded StokerKontrol to v3.25. But what should I do in the StokerKontrol program to get it online? Asks all sort of ftp stuff :s
There was one thing which was still old - boiler temp sensor - so replaced it this morning just to be sure again.
There was one thing which was still old - boiler temp sensor - so replaced it this morning just to be sure again.
Re: 16-24kw burner problems
I recommend downloading of StokerKontrol 3.5 because it is compatible with Stokercloud.
Du har ikke tilladelse til at få vist vedhæftede filer i dette indlæg.
-
- Stoker II
- 9
- Indlæg: 53
- Tilmeldt: 09 jan 2016 13:35
Re: 16-24kw burner problems
Ok, got the 3.5version up and running.
StokerCloud window, found it. The username and password...those I suppose to get from Nbe? They haven't responded to my email yet. Anyway tried with some random username and password and gave me an error into the Status box.
But when I tried to send myself a test email from Stokerkontrol then that arrived immediately.
StokerCloud window, found it. The username and password...those I suppose to get from Nbe? They haven't responded to my email yet. Anyway tried with some random username and password and gave me an error into the Status box.
But when I tried to send myself a test email from Stokerkontrol then that arrived immediately.